20.12.2022, 08:49
(13.12.2022, 11:51)admin Wrote: The status change most likely comes from a manual control. With the current logic it won't go back to low level until the light is manually switched off.
Thank you again!
I understand this thought, but I would still like to rule it out. To prove this, I first did a test.
To my knowledge there is no other action that puts the light at exactly 90%.
To test this, I set the value in the program to 85%. I had to restart the system for this to take effect. After this restart, the error remains the same, only the lamp is then set to 85% instead of 90%. I didn't change anything else, so I think I've confirmed that this script itself sets it to 85%.
Every day the lamp starts at 30% according to a different script.
I would like to know if this test is sufficient to show that the script itself chooses the higher value as the new setting, and if there is anything else I can try?