This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus device disconnected but can be read from read test
#8
Profile can be modified to use a single block read by setting read_count / read_offset parameters.
See these threads:
https://forum.logicmachine.net/showthrea...9#pid30319
https://forum.logicmachine.net/showthrea...8#pid19268

As for connection issues you might need to add read_delay to the profile.
Reply