This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Bacnet/ip LM 5 lite
#5
The value won't update automatically, you need to manually press scan. Mapping to objects has to be done via scripts. If you have several BACnet scripts running in parallel then direct connection must be used, see this post for an example: https://forum.logicmachine.net/showthread.php?tid=4530
Reply