You can't access a single port from multiple scripts at the same time, it will lead to errors. Enable RTU 1 and use mbproxy: https://forum.logicmachine.net/showthrea...53#pid1953
You might need to subtract 1 from the documented addresses as LM uses zero-based Modbus addresses. Use read test to check if addresses are correct.