Have you tested this with latest firmware?
The most likely cause is that LM is overloaded. Run this script and check the last column (drops) values. If at least one row has a non-zero value it means that a certain system part was unable to process incoming data quick enough. Receive buffer got full and certain messages got dropped.
To prevent this scripts must use grp.checkwrite/grp.checkupdate where applicable. Modbus send delta values and KNX filtering tables should be adjusted.
The most likely cause is that LM is overloaded. Run this script and check the last column (drops) values. If at least one row has a non-zero value it means that a certain system part was unable to process incoming data quick enough. Receive buffer got full and certain messages got dropped.
Code:
res = io.readfile('/proc/net/udp')
log(res)
To prevent this scripts must use grp.checkwrite/grp.checkupdate where applicable. Modbus send delta values and KNX filtering tables should be adjusted.