Trend clean
This example will change all valid trend values by x2. Recommended way of testing is to create a new trend log with the same parameters as the source.
infile = '/tmp/trends/t1.trend' outfile = '/tmp/trends/t7.trend' function adjust(value)   value = value * 2   return value end ffi = require('ffi') function stringtodouble(chunk)   local dbl = ffi.new('double[1]')   ffi.copy(dbl, chunk, 8)   return dbl[ 0 ] end function doubletostring(val)   local dbl = ffi.new('double[1]')   dbl[ 0 ] = val   return ffi.string(dbl, 8) end info = require('rrd').info(infile) data = io.readfile(infile) offset = info.header_size buf = { data:sub(1, offset) } while true do   chunk = data:sub(offset + 1, offset + 8)   if #chunk == 8 then     value = stringtodouble(chunk)     -- skip NaN (empty/undefined value)     if value == value then       value = adjust(value)     end     buf[ #buf + 1 ] = doubletostring(value)   else     break   end   offset = offset + 8 end data = table.concat(buf) io.writefile(outfile, data)
For counter type the editing is trickier. The stored value is not the actual counter value but a per-second change rate. This example will log the maximum of all stored values without writing to a different trend log file. You can use this value for replacement in the previous script.
infile = '/tmp/trends/t1.trend' max = 0 function check(value)   max = math.max(max, value) end ffi = require('ffi') function stringtodouble(chunk)   local dbl = ffi.new('double[1]')   ffi.copy(dbl, chunk, 8)   return dbl[ 0 ] end info = require('rrd').info(infile) data = io.readfile(infile) offset = info.header_size while true do   chunk = data:sub(offset + 1, offset + 8)   if #chunk == 8 then     value = stringtodouble(chunk)     -- skip NaN (empty/undefined value)     if value == value then       check(value)     end   else     break   end   offset = offset + 8 end log(max)
Note that when replacing values you should not use direct comparison (==) for floating point values due to possible rounding errors.
Trend clean - by domotiqa - 22.11.2023, 07:12
RE: Trend clean - by Daniel - 22.11.2023, 08:42
RE: Trend clean - by domotiqa - 22.11.2023, 08:51
RE: Trend clean - by Daniel - 22.11.2023, 08:54
RE: Trend clean - by domotiqa - 22.11.2023, 08:59
RE: Trend clean - by admin - 22.11.2023, 09:01
RE: Trend clean - by domotiqa - 22.11.2023, 09:25
RE: Trend clean - by domotiqa - 15.12.2023, 07:44
RE: Trend clean - by admin - 15.12.2023, 10:47
RE: Trend clean - by jmir - 31.05.2024, 05:58
RE: Trend clean - by domotiqa - 19.12.2023, 08:23
RE: Trend clean - by domotiqa - 19.12.2023, 16:39
RE: Trend clean - by admin - 31.05.2024, 06:51
RE: Trend clean - by jmir - 31.05.2024, 07:06
RE: Trend clean - by admin - 31.05.2024, 07:15
RE: Trend clean - by jmir - 31.05.2024, 14:17
RE: Trend clean - by domotiqa - 18.09.2024, 17:16
RE: Trend clean - by admin - 19.09.2024, 10:43
RE: Trend clean - by domotiqa - 20.09.2024, 10:12