This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus tcp-ip problem
#8
Last month I have used an Eliwell too, so I am almost sure that registers from 8000 are registers and not coil.
As admin say, you don't have to use 2 variables to read and write a register. I'll try to explain with an example:

{"name": "Temperatura Air Return", "bus_datatype": "9", "datatype": "int16", "type": "register", "address": 16391, "value_multiplier": 0.1, "writable": true},

if in your register 16391 there's the value 200°C, with the thet code you read 20,0°C and when you try to write, for example 30,5°C, in your PLC the homelynk will write 305°C.

Hope I was helpful Wink