Exactly what does CPU/IO measure, and how can you lower it?
Hi!
I have a two-fold question...
My setup: Wiser for KNX (HW 3) with firmware 3.0.0. Memory = 18%, Disk = 36%, KNX/TP load <2%. Appx 3500 objects (group addresses).
I do NOT use any of Touch 3, Cloud Connector, KNX IoT 3rd party API or any other app except "System load" and "Processes".
Instead I have created custom visualizations using .lp-files exclusively (I love the .lp format!).
Q1) Exactly what does the "CPU/IO" field in the bottom of the screen in Wiser for KNX / Configurator measure?
Is it a combination of CPU (processor) load and input/output (read/write) to the micro-sd/RAM memory?
I have spent the last couple of days trying to hunt down the source of recurring spikes when the value of CPU/IO jumps up from its idling level at about 0.02 to roughly 0.5 or sometimes even >1.0. It can stay at >0.3 for over 15-30 minutes and there seems to be no apparent pattern to when this happens (I have made a 5-minute Trend to monitor the first of the three CPU/IO values).
After installing the "sysload.ipk" found in another thread in this forum, it seems the total CPU load can be very low during these spikes - about 1-3% (including System) while at the same time the "CPU/IO" can hover around 0.3-0.5 for several minutes.
Q2) What are the most likely candidates to look for when trying to lower the CPU/IO?
For example, how efficient would it be to enforce these changes?
A) using grp.checkupdate() rather than grp.update()
B) avoid scheduling scripts to run at the exact same time
C) refactoring large user libraries, and break large files down into many smaller files
D) avoid 5-minute trends
E) avoid using more than ??? trends in total (any upper limit?)
Bottom line: should I take actions to troubleshoot when the CPU/IO goes >0.7 (the recommended limit in the manual) if it does so occasionally 4-5 times a day for 1-30 minutes at the time?
Sincerely,
Robert K
Exactly what does CPU/IO measure, and how can you lower it? - by temp4 - 09.04.2024, 01:48
