27.08.2024, 08:42
(27.08.2024, 08:27)Daniel Wrote: https://forum.logicmachine.net/showthrea...5#pid25655
Thanks. It shows load 80% on this:
Code:
lua lib/genohm-scada/core/scripting-resident.lua 1
I have only 4 resident scripts here, and by togging off and on consequently, I found this is Modbus Slave script (script is original, taken from this forum).
Seems, this because of we started using Modbus instead of Bacnet for communication with SCADA server.
But we have hundreds of other Modbus devices connected to the same SCADA server and no problems there.