Hi Zoltan,
The issue you know was related to Siemens TPUART2 and we switched a long time ago to newer version TPUART and have never seen it again, so i don't think your LM controller will stop soon..
Temperature messages are send when exceeding a threshold, not sure but i believe 40 or 50 degrees, can it be the controller is inside a cabinet and temperature is that high inside cabinet?
The other 2 messages are new to me, can it be that you have set object to bit and send bytes to it from KNX side?
BR,
Erwin