(23.01.2025, 11:28)admin Wrote: PID script needs to run in a loop to store the current state so scheduled script cannot be used.
Use a resident script with an extra os.sleep() at the end to make the total sleep interval longer.
Amazing. Thanks.
(23.01.2025, 11:28)admin Wrote: PID script needs to run in a loop to store the current state so scheduled script cannot be used.
Use a resident script with an extra os.sleep() at the end to make the total sleep interval longer.
One more question.
Should I still have it as resident with 60 seconds? will there not be a conflict if i do like this?
Quote:-- Resident: Golvvärme styrvärde regulator pid nedan:
-- Ange avrundningssteget här (t.ex. 0.1, 0.2, 0.25, 0.5, etc.)
local round_step = 0.20 -- Du kan ändra detta till det steg du vill ha.
-- Funktion för att avrunda till närmaste "step"
local function round_to_nearest(value, step)
return math.floor(value / step + 0.5) * step
end
-- Variabel för att slå på eller av temperaturskillnadskontrollen
local temperature_diff_enabled = false -- Sätt till 'true' för att kontrollera temperaturskillnaden, 'false' för att inaktivera
-- Hämta nuvarande och börvärde från sensorer och avrunda med angivet steg
local current_value = round_to_nearest(grp.getvalue('5/5/1'), round_step) -- Framledning ärvärde
local setpoint_value = round_to_nearest(grp.getvalue('5/5/0'), round_step) -- Framledning börvärde
-- Kontrollera temperaturskillnad efter avrundning
local temperature_diff = math.abs(setpoint_value - current_value)
local limit = 0.20 -- Gränsen för temperaturskillnad
-- Initiera PID om det behövs
if not p then
require('user.pid')
p = PID:init({
current = '5/5/1', -- Framledning ärvärde
setpoint = '5/5/0', -- Framledning börvärde
output = '5/5/15', -- GV styrvärde
round_step = round_step -- Här skickas round_step till PID
})
end
-- Kontrollera om temperaturskillnaden ska användas för att köra PID
if temperature_diff_enabled then
if temperature_diff > limit then
local previous_output = p.output
p:run()
if p.output ~= previous_output then
log(string.format("Styrvärde skickat till 5/5/15: %.2f (Ärvärde: %.2f, Börvärde: %.2f, Skillnad: %.2f°C)",
p.output, current_value, setpoint_value, temperature_diff))
end
else
log("Ingen signifikant avvikelse (" .. string.format("%.2f", temperature_diff) .. "°C), limit " .. string.format("%.2f", limit) .. "°C, PID ej körd. (Börvärde: " .. string.format("%.2f", setpoint_value) .. "°C, Ärvärde: " .. string.format("%.2f", current_value) .. "°C)")
end
else
local previous_output = p.output
p:run()
if p.output ~= previous_output then
log(string.format("Styrvärde skickat till 5/5/15: %.2f (Ärvärde: %.2f, Börvärde: %.2f, Skillnad: %.2f°C)",
p.output, current_value, setpoint_value, temperature_diff))
end
end
-- Lägg till en paus på 120000 millisekunder (2 minuter)
os.sleep(120000)