This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus RTU
#9
(25.03.2025, 14:52)admin Wrote: Your device doesn't have a GND connection. You can try adding a termination resistors on both line ends. Also check that LM power supply AC connection is correct (L/N are not swapped).

What line topology is used?

We have already tried with the final resistor since I read that the LM already has an internal one, daisy chain topology, 30 slaves, 38400 baudrate
Reply


Messages In This Thread
Modbus RTU - by Omega Technology - 25.03.2025, 14:31
RE: Modbus RTU - by admin - 25.03.2025, 14:32
RE: Modbus RTU - by Omega Technology - 25.03.2025, 14:35
RE: Modbus RTU - by admin - 25.03.2025, 14:40
RE: Modbus RTU - by Omega Technology - 25.03.2025, 14:45
RE: Modbus RTU - by admin - 25.03.2025, 14:47
RE: Modbus RTU - by Omega Technology - 25.03.2025, 14:48
RE: Modbus RTU - by admin - 25.03.2025, 14:52
RE: Modbus RTU - by Omega Technology - 25.03.2025, 14:56
RE: Modbus RTU - by admin - 25.03.2025, 14:58
RE: Modbus RTU - by Omega Technology - 25.03.2025, 14:59
RE: Modbus RTU - by admin - 25.03.2025, 15:21
RE: Modbus RTU - by Omega Technology - 26.03.2025, 10:40
RE: Modbus RTU - by admin - 26.03.2025, 10:43
RE: Modbus RTU - by Omega Technology - 26.03.2025, 11:42
RE: Modbus RTU - by Omega Technology - 27.03.2025, 07:17
RE: Modbus RTU - by Daniel - 26.03.2025, 11:44
RE: Modbus RTU - by Omega Technology - 26.03.2025, 17:12
RE: Modbus RTU - by Daniel - 27.03.2025, 08:25