This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus TCP Slave Problem
#2
The recommended way is to use profiles instead of scripts: https://forum.logicmachine.net/showthread.php?tid=5911

Each value for writemultipleregisters is passed as a separate argument, not a table:
Code:
mb:writemultipleregisters(32, 1) mb:writemultipleregisters(33, 1)

You can write to both registers with one call:
Code:
mb:writeregisters(32, 1, 1)
Reply


Messages In This Thread
Modbus TCP Slave Problem - by JaegerMa2 - 17.06.2025, 06:50
RE: Modbus TCP Slave Problem - by admin - 17.06.2025, 07:42
RE: Modbus TCP Slave Problem - by khalil - 15.09.2025, 11:15
RE: Modbus TCP Slave Problem - by admin - 15.09.2025, 11:20
RE: Modbus TCP Slave Problem - by khalil - 15.09.2025, 11:24
RE: Modbus TCP Slave Problem - by admin - 15.09.2025, 11:27
RE: Modbus TCP Slave Problem - by khalil - 15.09.2025, 11:38