This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

VAV logic
#3
I have 8 VAV dampers (2 per floor) that are controlled using a 0–100% command, corresponding to vMin–vMax.
Currently, some of the VAV dampers have the same vMin and vMax values, but this may change later.

When there is a cooling command, the corresponding VAV damper should switch to vMax = 100% in summer mode.
When this change to vMax occurs, I also need to increase the setpoint of the ventilation system accordingly.

Example – Setpoint Airflow Calculation:
Cooling Command Status Value
Cooling Cmd 1 Not active 250
Cooling Cmd 2 Active 650
Cooling Cmd 3 Active 850
Cooling Cmd 4 Not active 180

Resulting ventilation system setpoint = 1930

The 70% that i first decribe i see was wrong. I have change that part now i the main topic.