This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Error using 255 byte string and ETS5
#2
Hi,

The 255 byte is no KNX standard dpt. However it's send over KNX IP to be able to send data to another controller. grp.update only blocks telegram to TP so when your ETS is connected over IP you will get invalid dpt telegram in the monitor, so your solution to block it in filter does do the trick. Keep in mind that your telegram will not reach other controllers now.

BR,

Erwin