(13.08.2025, 15:51)Daniel Wrote: Can you provide remote access? If yes send me PM.
Double check the cable next to LM.
Did you check the voltage on LM side of TP connector?
Of course I can, but wait a second. I think I found the problem. It seems that the KNX connector is damaged and is not making contact with the LM5 terminal.
I’m looking for another terminal block in the van and will do some tests.
(13.08.2025, 16:03)Gabriel88 Wrote:(13.08.2025, 15:51)Daniel Wrote: Can you provide remote access? If yes send me PM.
Double check the cable next to LM.
Did you check the voltage on LM side of TP connector?
Of course I can, but wait a second. I think I found the problem. It seems that the KNX connector is damaged and is not making contact with the LM5 terminal.
I’m looking for another terminal block in the van and will do some tests.
Update: it really seems that the KNX terminal block on the LM5 was faulty. After replacing it, everything appears to be working, and I can also use the LM5 as an interface for ETS. Conclusion: machine update is all good, the problem was on my side due to the faulty terminal block. I don’t know how to thank you enough for your advice and patience... Drinks are on me!