Zerotier
#26
(05.06.2025, 09:43)Daniel Wrote: LM supports BACnet so this will work on both platforms. If controller is on different subnet we also support FDR, see BBMD settings in BACnet settings.
I am trying to integrate a device running on the 192.168.63.0/24 network with a BACnet/IP system on the 211.67.63.0/24 network. The setup is as follows:
  • BACnet server device: 192.168.63.162 (should register as Foreign Device)
  • BBMD (BACnet client/PLC): 211.67.63.171
  • Port: 47808
  • Device ID: 127001
Configuration
On the server side (192.168.63.162), I configured:
  • BBMD IP = 211.67.63.171
  • BBMD Port = 47808
  • TTL = 180 seconds
Tests performed
I have a PC in each network. I tried to add a special firewall rule on port 47808, and even to deactivate the firewalls on both PCs
  • With Wireshark running on the server’s network interface:
    • I can see “unconfirmed-req I-Am device, 127001” at startup.
    • I do not see any BVLC: Register-Foreign-Device (function 0x05) messages sent to 211.67.63.171.
  • With Wireshark on the BBMD side (211.67.63.0/24):
    • The BBMD sends Who-Is requests for device 127001.
It seems to me that it can not be a network admin issue since the request is not even issued as we have  no Register-Foreign-Device frames visible.
Is there something that should be done to activate the FDR function, appart from filling the 3 last fields of the BACnet server setting page?
Kind Regards
Zerotier - by guillermo - 19.09.2024, 12:33
RE: Zerotier - by Daniel - 19.09.2024, 12:44
RE: Zerotier - by kyxsinea - 20.09.2024, 10:10
RE: Zerotier - by Daniel - 20.09.2024, 10:15
Zerotier - by guillermo - 23.09.2024, 09:40
RE: Zerotier - by admin - 24.09.2024, 07:33
RE: Zerotier - by bgb - 24.09.2024, 12:16
RE: Zerotier - by guillermo - 25.09.2024, 05:35
RE: Zerotier - by Daniel - 24.09.2024, 12:45
RE: Zerotier - by bgb - 25.09.2024, 07:11
RE: Zerotier - by admin - 25.09.2024, 07:29
RE: Zerotier - by guillermo - 30.09.2024, 05:30
RE: Zerotier - by Daniel - 30.09.2024, 07:40
RE: Zerotier - by Bba - 05.06.2025, 08:43
RE: Zerotier - by Daniel - 05.06.2025, 08:47
RE: Zerotier - by Bba - 05.06.2025, 08:54
RE: Zerotier - by Daniel - 05.06.2025, 08:56
RE: Zerotier - by Bba - 05.06.2025, 08:58
RE: Zerotier - by Daniel - 05.06.2025, 09:23
RE: Zerotier - by Bba - 05.06.2025, 09:34
RE: Zerotier - by Daniel - 05.06.2025, 09:43
RE: Zerotier - by Bba - 05.06.2025, 11:23
Foreign Device Registration not working – no Register-Foreign-Device frames visible - by fee_connect - 25.09.2025, 20:49
RE: Zerotier - by Zoli - 12.09.2025, 08:13
RE: Zerotier - by Daniel - 12.09.2025, 08:18
RE: Zerotier - by Zoli - 12.09.2025, 08:28
RE: Zerotier - by Daniel - 26.09.2025, 07:00
RE: Zerotier - by admin - 26.09.2025, 07:25
RE: Zerotier - by fee_connect - 26.09.2025, 12:17
RE: Zerotier - by admin - 26.09.2025, 12:42
RE: Zerotier - by fee_connect - 30.09.2025, 21:11
RE: Zerotier - by Daniel - 01.10.2025, 07:20
RE: Zerotier - by Bba - 10.02.2026, 07:19
RE: Zerotier - by admin - 10.02.2026, 07:21