This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Schneider Energy Meters Modbus Readings
#6
In RTU read test set address to 43914 (frequency) and data type to float32. Then try reading values with different read swap parameters. When you find correct read swap value set it in profile as stated here: http://openrb.com/docs/modbus.htm

Quote:Possible string values: n (no swap), w (word swap), b (byte swap), bw (byte and word swap)
Reply


Messages In This Thread
RE: Schneider Energy Meters Modbus Readings - by admin - 24.10.2017, 07:15