TCP Modbus
(29.11.2017, 17:15)admin Wrote: What value are you getting? Try setting read_swap to b, datatype should be set to uint16, bus_datatype can be float16 and set value_multiplier to 0.01
Thank you! Setting value_multiplier to 0.01 helped.
For everyone who use Komfovent Ping2 (modbus gateway for Komfovent ventilation AHU) my profile in attachment.
.json   Komfovent_Ping2.json (Size: 2.48 KB / Downloads: 45)
TCP Modbus - by leondias - 21.03.2017, 14:08
RE: TCP Modbus - by admin - 21.03.2017, 14:34
RE: TCP Modbus - by leondias - 21.03.2017, 14:39
RE: TCP Modbus - by unaxboy - 29.11.2017, 12:44
RE: TCP Modbus - by admin - 21.03.2017, 14:42
RE: TCP Modbus - by leondias - 21.03.2017, 14:47
RE: TCP Modbus - by admin - 21.03.2017, 15:59
RE: TCP Modbus - by leondias - 22.03.2017, 07:38
RE: TCP Modbus - by unaxboy - 13.11.2017, 04:18
RE: TCP Modbus - by admin - 29.11.2017, 13:09
RE: TCP Modbus - by unaxboy - 29.11.2017, 13:32
RE: TCP Modbus - by admin - 29.11.2017, 13:35
RE: TCP Modbus - by unaxboy - 29.11.2017, 13:55
RE: TCP Modbus - by admin - 29.11.2017, 15:54
RE: TCP Modbus - by unaxboy - 29.11.2017, 16:47
RE: TCP Modbus - by admin - 29.11.2017, 17:15
RE: TCP Modbus - by unaxboy - 29.11.2017, 18:22
RE: TCP Modbus - by Igor68 - 17.12.2017, 10:22
RE: TCP Modbus - by admin - 18.12.2017, 08:09
RE: TCP Modbus - by SportMaster10 - 12.09.2019, 11:20
RE: TCP Modbus - by AlexLV - 02.07.2020, 08:10
RE: TCP Modbus - by Daniel - 02.07.2020, 08:28
RE: TCP Modbus - by AlexLV - 03.07.2020, 06:56
RE: TCP Modbus - by AlexLV - 03.07.2020, 19:30