(29.11.2017, 17:15)admin Wrote: What value are you getting? Try setting read_swap to b, datatype should be set to uint16, bus_datatype can be float16 and set value_multiplier to 0.01
Thank you! Setting value_multiplier to 0.01 helped.
For everyone who use Komfovent Ping2 (modbus gateway for Komfovent ventilation AHU) my profile in attachment.