This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Resident script pump circulation
#6
1. Add tag valve to your valve objects. Create an event script that is mapped to valve tag:
Code:
-- get OR'ed value of all tagged objects value = false objects = grp.tag('valve') for _, object in ipairs(objects) do   value = value or object.value end if value then   -- save pump timer if timer has not been started yet   time = storage.get('pump_on_time', 0)   if time == 0 then     storage.set('pump_on_time', os.time())   end else   -- turn pump off   storage.set('pump_on_time', 0)   grp.checkwrite('pump', false) end

2. Create either a resident script with large sleep time or a scheduled script that runs every minute:
Code:
-- turn pump on when time delta >= 5 minutes time = storage.get('pump_on_time', 0) if time > 0 then   delta = os.time() - time   if delta >= 5 * 60 then     grp.checkwrite('pump', true)   end else   grp.checkwrite('pump', false) end

In both scripts replace pump with pump object name or group address.
Reply


Messages In This Thread
RE: Resident script pump circulation - by admin - 08.03.2018, 12:46