12.07.2018, 11:42
(12.07.2018, 11:29)buuuudzik Wrote: For this module this is enough configuration:Line 10
EnOcean->KNX: F6-02-01 (first object S2, second S1)
KNX->EnOcean: F6-01-03 (connect on/off to only first object to control relay; select "Send telegram")
One device is controlled via such set of objects:
Zone 1_on/off - command object from LM true = on, false = off
Zone 1_trigger 1 - status of click (used for update the Zone 1_status)
Zone 1_trigger 2 - status of click (used for switching other object)
Zone 1_status - calculated relay status
These objects should have tag e.g. "enocean_st":
Zone 1_on/off
Zone 1_trigger 1
This script should be connected to above tag "enocean_st":
Code:-- Updating relay state value = event.getvalue() alias = grp.alias(event.dst) zone, mode = alias:match('(.*)_(.*)') statusAlias = zone .. '_status' status = grp.getvalue(statusAlias) if mode == 'toggle 1' then grp.write(statusAlias, not status) elseif mode == 'on/off' then grp.write(statusAlias, value) end
'toggle 1' or should it be 'trigger 1' ?
------------------------------
Ctrl+F5