25.07.2018, 11:00
(25.07.2018, 10:13)josep Wrote: Hello,
Thank you very much for your responses. I have an LM5Lp so I have used the imx6 file (I understand that it is the processor that carries the lite power) once this is done I have rebooted the Logic Machine but everything remains the same, if I go to the Modbus option I only see one of the two ports of which the equipment has, any solution? Thank you very much.
go to system configuration - system - packages and check ghenom-scada-modbus version. it should be 20171103. if it's not press "green plus" button and install package.
if it is 20171103, try to clear browser cache.
just checked on my lm5 (see attach)