		Hi Gert Jan,
When you have 2 devices in the same line that has a TP and also a IP connection you create a loop, any telegram on the TP is repeated on the IP side and then the other device puts it from IP to the TP again (infinity loop). Basically you create a double line/backbone. Only solution to this is disable KNX IP in one of the 2 devices.
BR,
Erwin
	
	
	
When you have 2 devices in the same line that has a TP and also a IP connection you create a loop, any telegram on the TP is repeated on the IP side and then the other device puts it from IP to the TP again (infinity loop). Basically you create a double line/backbone. Only solution to this is disable KNX IP in one of the 2 devices.
BR,
Erwin
 
 