This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

2 byte error message
#1
Hello (again)!

I have a UK24EIB Gateway which has a 2byte error message for each MP-Address.

Error codes for High-Byte: 
0b0000’0000 = No error present 
0b0000’0001 = Connected actuator does not correspond to parameterised type 
0b0000’0010 = No communication possible at this address 
0b0000’0100 = Connected actuator signalling error, see Low-Byte 
0b0000’1000 = No valid Min / Max values 
0b0001’0000 = Non-Hall sensor motor actuators only: Actuator not yet synchronised 
0b0010’0000 = Test run active 
0b0100’0000 = Monitoring time of reference value elapsed 
0b1000’0000 = Not used Several errors can be present together, OR-gated bitwise 

Error codes for Low-Byte: 
0b0000’0000 = No error present 
0b0000’0001 = Stop & Go ratio 
0b0000’0010 = Increased position travel 
0b0000’0100 = Overload, reference position not attained 
0b0000’1000 = No support at present 

The first 4 Bits are always 0. Several errors can be present together, OR-gated bitwise