This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Remaining time or counter
#41
Hello, using this great script I would like to modify it with your help.

So far this script is executed with the detection object. In my case, this object, through another script, is just a 1-second toggle to correct issues that sometimes occur when the detector does not send 'no detection'. The output object is modified with a checkwrite so that it only sends it once.

On the other hand, I have a Lock object and I want to use it to lock the detector and this script.

I would like if it is possible that this Blocking object, apart from blocking the script, could reset the time to zero and not modify the output object..



Code:
-- Set output address
AddressOutput = '39/0/1' -- 01. 1 bit (boolean)

--ID Detector Zone
i = 1

-- Set input address
AddressInput = '9/1/'..i -- 01. 1 bit (boolean)

-- Set external time address (optional)
AddressExternalTime = '38/1/'..i -- 07. 2 byte unsigned integer

-- Set feedback adress of time left indication (optional)
AddressTimeLeft = '38/2/'..i -- 255 byte string

-- Seconds or Minutes
SetSec = '38/3/'..i -- Set to false for Minutes or true for seconds

-- Set blocking address
AddressBlocking = '38/4/'..i -- 01. 1 bit (boolean)

-- Use time left indication
UseTimeLeft = true -- Set to false if no time left indication is used

-- Set time delay (Used when external time is not available)
SetDelay = 120 -- 2 minutes

-- Set factor delay (Multiplies Delay)
SetFac = 1

-- Logic can be turned of by value 0
Off_by_Value_Zero = false




-- ************************************** END PARAMETERS ************************************ --
-- *************************** DON'T CHANGE ANYTHING UNDER THIS LINE ************************ --


Input_Value = event.getvalue()
if Off_by_Value_Zero == false and (Input_Value == false or Input_Value == 0) then
return
else
tpid = storage.get('PID:' .. _SCRIPTNAME)
if tpid == nil then
     pid = os.getpid()
     storage.set('PID:' .. _SCRIPTNAME, pid)
else
   pid = os.getpid()  
   storage.set('PID:' .. _SCRIPTNAME, pid)
   os.kill(tpid, signal.SIGKILL)
end
 
blocking = grp.getvalue(AddressBlocking)
if not blocking then
   return
end

 
function Calculate_Time(StairCaseTime)
   if StairCaseTime > (86400 -1) then
     StairCaseTime = (86400 -1)
   end
   local hours = math.floor(StairCaseTime / 3600 % 24)
   local minutes = math.floor(StairCaseTime / 60 % 60)
   local seconds = math.floor(StairCaseTime % 60)
   time = {
     day = 0,
     hour = hours,
     minute = minutes,
     second = seconds,
   }
   time =string.format('%02d:%02d:%02d',time.hour,time.minute,time.second)
   return time
end
if Input_Value == true or Input_Value == 1 then
   ValueExternalTime = grp.getvalue(AddressExternalTime) or SetDelay
   if grp.getvalue(SetSec) then
    Multiply_Seconds = 1
   else
     Multiply_Seconds = 60
    end
   StairCaseTime = ValueExternalTime * Multiply_Seconds * SetFac
   grp.checkwrite(AddressOutput, true)
   if UseTimeLeft == true then
     if StairCaseTime > 0 then
       time = Calculate_Time(StairCaseTime)
       grp.write(AddressTimeLeft, time)
       repeat
         StairCaseTime = StairCaseTime - 1
         time = Calculate_Time(StairCaseTime)
         grp.write(AddressTimeLeft, time)
         os.sleep(1)
       until StairCaseTime == 0
     end   
   else
     os.sleep(StairCaseTime)
   end
   grp.write(AddressOutput, false)
elseif Input_Value == false or Input_Value == 0 then
   ValueOutput = grp.getvalue(AddressOutput)
   if ValueOutput == false then
     if UseTimeLeft == true then
       time = Calculate_Time(0)
       grp.write(AddressTimeLeft, time)
     end
     grp.write(AddressOutput, false)
   end
end
storage.delete('PID:' .. _SCRIPTNAME)
end
Reply


Messages In This Thread
Remaining time or counter - by Tokatubs - 15.12.2018, 21:29
RE: Remaining time or counter - by Tokatubs - 16.12.2018, 00:51
RE: Remaining time or counter - by AlexLV - 16.12.2018, 16:09
RE: Remaining time or counter - by AlexLV - 16.12.2018, 20:59
RE: Remaining time or counter - by Tokatubs - 18.12.2018, 19:35
RE: Remaining time or counter - by AlexLV - 19.12.2018, 22:14
RE: Remaining time or counter - by Thomas - 20.12.2018, 10:13
RE: Remaining time or counter - by admin - 20.12.2018, 10:54
RE: Remaining time or counter - by Tokatubs - 20.12.2018, 22:27
RE: Remaining time or counter - by Daniel - 21.12.2018, 08:42
RE: Remaining time or counter - by Tokatubs - 21.12.2018, 09:28
RE: Remaining time or counter - by Daniel - 21.12.2018, 12:18
RE: Remaining time or counter - by Daniel - 21.12.2018, 13:11
RE: Remaining time or counter - by Tokatubs - 21.12.2018, 22:54
RE: Remaining time or counter - by AlexLV - 24.12.2018, 17:00
RE: Remaining time or counter - by CHOUAIBOU - 25.12.2018, 13:24
RE: Remaining time or counter - by AlexLV - 26.12.2018, 09:05
RE: Remaining time or counter - by AlexLV - 06.01.2019, 23:05
RE: Remaining time or counter - by admin - 29.01.2020, 11:28
RE: Remaining time or counter - by admin - 29.01.2020, 13:34
RE: Remaining time or counter - by AlexLV - 30.01.2020, 07:14
RE: Remaining time or counter - by AlexLV - 30.01.2020, 12:41
RE: Remaining time or counter - by davidchispas - 20.04.2022, 08:48
RE: Remaining time or counter - by admin - 09.08.2022, 08:20
RE: Remaining time or counter - by admin - 09.08.2022, 10:09
RE: Remaining time or counter - by Novodk - 26.05.2023, 19:46
RE: Remaining time or counter - by Novodk - 27.05.2023, 07:02
RE: Remaining time or counter - by admin - 27.05.2023, 06:59
RE: Remaining time or counter - by admin - 27.05.2023, 07:06
RE: Remaining time or counter - by Novodk - 27.05.2023, 07:18
RE: Remaining time or counter - by admin - 29.05.2023, 08:29
RE: Remaining time or counter - by Novodk - 29.05.2023, 08:52
RE: Remaining time or counter - by FatMax - 29.05.2023, 09:04
RE: Remaining time or counter - by Novodk - 01.06.2023, 16:26

Forum Jump: