This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

LM5 Modbus TCP
#4
Are you sure about port 10502? Default modbus port is 502.
Reply


Messages In This Thread
LM5 Modbus TCP - by OysteinEl - 28.09.2020, 06:33
RE: LM5 Modbus TCP - by admin - 28.09.2020, 06:37
RE: LM5 Modbus TCP - by OysteinEl - 28.09.2020, 07:01
RE: LM5 Modbus TCP - by admin - 28.09.2020, 07:04
RE: LM5 Modbus TCP - by OysteinEl - 28.09.2020, 07:14
RE: LM5 Modbus TCP - by admin - 28.09.2020, 07:31
RE: LM5 Modbus TCP - by OysteinEl - 28.09.2020, 08:14
RE: LM5 Modbus TCP - by admin - 28.09.2020, 09:11
RE: LM5 Modbus TCP - by OysteinEl - 28.09.2020, 09:25
RE: LM5 Modbus TCP - by OysteinEl - 28.09.2020, 11:50
RE: LM5 Modbus TCP - by admin - 28.09.2020, 12:40
RE: LM5 Modbus TCP - by OysteinEl - 28.09.2020, 12:59
RE: LM5 Modbus TCP - by admin - 28.09.2020, 13:30
RE: LM5 Modbus TCP - by OysteinEl - 29.09.2020, 06:51
RE: LM5 Modbus TCP - by admin - 29.09.2020, 12:22

Forum Jump: