This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Display time of object
#4
You will need two scripts for this.
1. Event script mapped to control or status object if the load:
Code:
value = event.getvalue()
key = 'ontime'
out = '32/1/5'

if value then
  if not storage.get(key) then
    storage.set(key, os.time())
    grp.update(out, '0m')
  end
else
  storage.delete(key)
  grp.update(out, '')
end

2. Scheduled script that runs every minute:
Code:
key = 'ontime'
out = '32/1/5'

time = storage.get(key)
if time then
  delta = os.time() - time
  minutes = math.floor(delta / 60)
  
  hours = math.floor(minutes / 60)
  minutes = minutes % 60

  if hours > 0 then
    res = hours .. 'h '
  else
    res = ''
  end
  
  res = res .. minutes .. 'm'
  grp.update(out, res)
end

32/1/5 is the object that shows the load ON time, set data type to 250 byte string. If you need multiple status outputs then use a unique storage key for each load (ontime in this example).
Reply


Messages In This Thread
Display time of object - by Nir70 - 22.12.2021, 17:50
RE: Display time of object - by admin - 23.12.2021, 08:41
RE: Display time of object - by Nir70 - 23.12.2021, 08:47
RE: Display time of object - by admin - 23.12.2021, 09:32
RE: Display time of object - by Nir70 - 23.12.2021, 11:22
RE: Display time of object - by Dré - 27.12.2021, 15:03
RE: Display time of object - by admin - 23.12.2021, 11:46
RE: Display time of object - by Nir70 - 23.12.2021, 12:21
RE: Display time of object - by admin - 23.12.2021, 12:30
RE: Display time of object - by Dré - 24.12.2021, 15:49
RE: Display time of object - by khalil - 26.12.2021, 08:28
RE: Display time of object - by Nir70 - 23.12.2021, 14:49
RE: Display time of object - by admin - 23.12.2021, 14:52
RE: Display time of object - by Nir70 - 23.12.2021, 16:50
RE: Display time of object - by admin - 24.12.2021, 08:51
RE: Display time of object - by Nir70 - 27.12.2021, 20:25
RE: Display time of object - by admin - 28.12.2021, 08:31
RE: Display time of object - by Dré - 28.12.2021, 12:34
Display time of object - PCU heat - by Nir70 - 29.12.2021, 15:59
RE: Display time of object - by admin - 29.12.2021, 16:04
RE: Display time of object - by Nir70 - 29.12.2021, 16:19
RE: Display time of object - by admin - 29.12.2021, 16:35
RE: Display time of object - by Dré - 30.12.2021, 13:24
RE: Display time of object - by admin - 05.04.2022, 13:02
RE: Display time of object - by Rauschentofft - 03.11.2022, 23:35
RE: Display time of object - by admin - 04.11.2022, 08:26
RE: Display time of object - by Rauschentofft - 04.11.2022, 09:26
RE: Display time of object - by nmedalacabeza - 01.01.2023, 18:31
RE: Display time of object - by admin - 02.01.2023, 08:47
RE: Display time of object - by nmedalacabeza - 02.01.2023, 19:21
RE: Display time of object - by Daniel - 03.01.2023, 08:58
RE: Display time of object - by nmedalacabeza - 04.01.2023, 08:54
RE: Display time of object - by admin - 04.01.2023, 08:56
RE: Display time of object - by nmedalacabeza - 04.01.2023, 10:50
RE: Display time of object - by admin - 05.01.2023, 08:13
RE: Display time of object - by nmedalacabeza - 07.01.2023, 17:28
RE: Display time of object - by nmedalacabeza - 21.01.2023, 20:35
RE: Display time of object - by admin - 23.01.2023, 08:16
RE: Display time of object - by nmedalacabeza - 23.01.2023, 16:28
RE: Display time of object - by admin - 23.01.2023, 16:32
RE: Display time of object - by nmedalacabeza - 23.01.2023, 16:54
RE: Display time of object - by admin - 24.01.2023, 07:10

Forum Jump: