This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Can BUS
#6
(02.06.2022, 05:47)admin Wrote: What power supply for DALI are you using? And how long is the DALI line?

RX (collision) error can happen if several ballasts have the same short address or the ballast transmitting voltage is not low enough to be detected by the gateway. We've seen some ballasts that do not follow the minimums required by the DALI standard.

If you enable status object for a ballast then the current output value will be polled automatically from time to time.


This is the font, I have it installed in several projects without problems:
https://www.sunricher.com/dali-power-sup...2400p.html



We have frames per floor, so the dali line distance is short, in addition the ballasts are located in two or three points but relatively close.

Is it possible to identify which ballasts are causing the problem? The assignment of the short addresses was made with all the ballasts connected and the ignitions were perfectly identified.

The status object is enabled in all the ballasts, so the traffic of those objects is normal, I thought that it was only sent when the status changed.
Reply


Messages In This Thread
Can BUS - by DGrandes - 20.05.2022, 07:18
RE: Can BUS - by admin - 20.05.2022, 08:18
RE: Can BUS - by CristianAgata - 20.05.2022, 10:00
RE: Can BUS - by davidchispas - 01.06.2022, 13:39
RE: Can BUS - by admin - 02.06.2022, 05:47
RE: Can BUS - by davidchispas - 02.06.2022, 07:51
RE: Can BUS - by davidchispas - 02.06.2022, 10:12
RE: Can BUS - by admin - 02.06.2022, 10:31
RE: Can BUS - by davidchispas - 02.06.2022, 13:03
RE: Can BUS - by admin - 03.06.2022, 06:09
RE: Can BUS - by davidchispas - 03.06.2022, 07:51
RE: Can BUS - by davidchispas - 03.06.2022, 06:20
RE: Can BUS - by admin - 03.06.2022, 10:21
RE: Can BUS - by davidchispas - 08.06.2022, 08:22
RE: Can BUS - by davidchispas - 08.07.2022, 09:38
RE: Can BUS - by admin - 08.07.2022, 09:43

Forum Jump: