Too long since last update
I would like to do the following:
- tag all temperature readings
- search up these temperature readings that are tagged
- get the oldest timestamp
- if timestamp is older than two hours
= write a boolean 1 on a group address
This way I could indicate that there is a sensor on my installation that is not sending the current temperature anymore.
Hope this could be done with a script. In advance thanks.  Cool
-CDG
I think you need something like this:
output = false max_timestamp = os.time() - 7200 -- 2 hours in seconds for _, object in ipairs(grp.tag('temperature')) do  if object.updatetime < max_timestamp then    output = true    break  end end grp.checkwrite('1/1/1', output)
That did the trick! Thank you very much.  Smile