Wiser - transfer string over BACnet IP
I have project with Wiser and I need to transfer error codes (written in the KNX bus - 14 byte ASCII string) over BACnet IP to the workstation. The problem is that Wiser does not support transfer of string characters over BACnet. The error codes are fixed - about 30, for example "7H-01", "BH-00", etc. I want to make script in the Wiser to code the string in some integer value and then transfer this value over BACnet.
I've tried to use string.match but I had no success. I will appreciate any suggestions how this could be achieved.
Just create a event based script on the KNX object and write a value to a virtual object and attach this script to it (now for 6 variable so you need to extend it):
value = event.getvalue() if value == '7H-01' then     grp.update('32/0/0', 1) elseif value == 'BH-00' then     grp.update('32/0/0', 2) elseif value == 'BH-01' then     grp.update('32/0/0', 3) elseif value == 'BH-02' then     grp.update('32/0/0', 4) elseif value == 'BH-03' then     grp.update('32/0/0', 5) elseif value == 'BH-04' then     grp.update('32/0/0', 6) end
Inside the ES/AS you can create a trigger based script to decode them back to a string object.