On this new installation the LM is randomly restarting for a last few days. But only a few times a day. Load averages: 0.49 0.45 0.36 at the moment.
It here any way to catch the reboot cause? TP is not connected, KNX connection is via N146/02, no visu, just a few scipts.
Threads: 31
What about Memory ?
Threads: 31
You can try to log CPU/IO and memory but if device just reboot you could loose up to last 30 mins.
It could be also HW issue.
data = io.readfile('/proc/meminfo')
load = io.readfile('/proc/loadavg'):split(' ')[ 1 ]
memtotal = data:match('MemTotal:%s+(%d+)')
memavail = data:match('MemAvailable:%s+(%d+)')
memusage = math.floor((memtotal - memavail) / memtotal * 1000) / 10
log(load, memusage)
Threads: 103
According to my experience KNX packet loop through multicast IP triggers reboot very quickly. Plus you lost evidence and the source of the problem which makes it hard to discover the issue.