rewrite
I use scripts to read or write BACNET values.
I would like to know if there is an easy way to rewrite this script more clearly and not send the values every time (If the value read on the BACNET is the same as the previous one then we do not rewrite it) :
require('bacnet') --CASSETTE 2 value2 = bacnet.readvalue(16002, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/2', value2) --CASSETTE 3 value3 = bacnet.readvalue(16003, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/3', value3) --CASSETTE 4 value4 = bacnet.readvalue(16004, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/4', value4) --CASSETTE 5 value5 = bacnet.readvalue(16005, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/5', value5) --CASSETTE 6 value6 = bacnet.readvalue(16006, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/6', value6) --CASSETTE 7 value7 = bacnet.readvalue(16007, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/7', value7) --CASSETTE 8 value8 = bacnet.readvalue(16008, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/8', value8) --CASSETTE 9 value9 = bacnet.readvalue(16009, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/9', value9) --CASSETTE 10 value10 = bacnet.readvalue(16010, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/10', value10) --CASSETTE 11 value11 = bacnet.readvalue(16011, 'binary value', 8) -- Prise du statut Fenetre grp.write('5/3/11', value11)
This script is one of the resident scripts for reading values I have many and some are for writing.
B.R.
You can use for loop and checkwrite which will not send the same value again.
require('bacnet') for i = 2, 11 do   id = 16000 + i   value = bacnet.readvalue(id, 'binary value', 8) -- Prise du statut Fenetre   grp.checkwrite('5/3/' .. i, value) end
(09.08.2019, 06:34)admin Wrote: You can use for loop and checkwrite which will not send the same value again.
Thanks !!