This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

limits when LM as Modbus TCP slave
#1
Thanks a lot for the LM resident script like Modbus TCP slave! We can use 125 registers at a time, right? what can i do if i need to read / write more registers? what are the limitations in this?
Reply
#2
125 registers is ModBus standard limit. But it only applies to a single request. If you want to read/write more then send several requests.
Reply
#3
(25.11.2020, 10:22)admin Wrote: 125 registers is ModBus standard limit. But it only applies to a single request. If you want to read/write more then send several requests.
thanks! but what about addressing with multiple requests? will the address of the first register in the second request be 0 again? oh, understand Smile addressing continues
Reply
#4
Each read request has a starting address and a number of coils/registers to read. The starting address is an absolute value and it does not matter which address was used in previous request.
Reply
#5
so no limits? 65536 registers can be polled?
Reply
#6
Yes, the whole range can be used.
Reply
#7
thank you!