This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

bacnet package last version
#1
Where can I download the last version of the bacnet package?

Thanks
Reply
#2
https://dl.openrb.com/lm-19-imx6/pkg/
------------------------------
Ctrl+F5
Reply
#3
(11.06.2020, 13:14)Daniel. Wrote: https://dl.openrb.com/lm-19-imx6/pkg/

Which package is the correct one?

I want to use the LM as Bacnet client. Is this info obsolete? https://openrb.com/logicmachine-as-bacnet-client/
Reply
#4
https://dl.openrb.com/lm-19-imx6/pkg/gen...8_imx6.ipk
There is also bacnet client app in the app store.
------------------------------
Ctrl+F5
Reply
#5
(11.06.2020, 13:19)Daniel. Wrote: https://dl.openrb.com/lm-19-imx6/pkg/gen...8_imx6.ipk
There is also bacnet client app in the app store.

Thanks so much.

I want to map the bacnet objects to knx. There's any manual?
Reply
#6
If you use the app, then there is no need for a manual, if you want to use our old way with scripts then you posted link to the instructions above.
------------------------------
Ctrl+F5
Reply
#7
(11.06.2020, 13:25)Daniel. Wrote: If you use the app, then there is no need for a manual, if you want to use our old way with scripts then you posted link to the instructions above.

You can assign a knx address to the bacnet objects directly in the app?

There's any place where I can see images of this configuration?
Reply
#8
https://www.screencast.com/t/dwxukrHU8bxv
------------------------------
Ctrl+F5
Reply
#9
(11.06.2020, 16:22)Daniel. Wrote: https://www.screencast.com/t/dwxukrHU8bxv

Thank you very much Daniel.
Reply
#10
(11.06.2020, 13:19)Daniel. Wrote: https://dl.openrb.com/lm-19-imx6/pkg/gen...8_imx6.ipk
There is also bacnet client app in the app store.
Daniel Hi,

I have installed the application from the store. I am using the specific Lmachine as a client (server is disabled) but during scanning, no BACnet devices were discovered.  
At the same network, there is a LMachine working as a server, 4 Siemens BACnet devices, and a BACnet Management Station.
Is there something more to check in order for the plug-in to successfully discover BACnet devices?
Reply
#11
Which firmware version and bacnet package (not genohm-scada-bacnet) version do you have?
Reply
#12
(30.11.2020, 07:17)admin Wrote: Which firmware version and bacnet package (not genohm-scada-bacnet) version do you have?

I'm sorry for the delayed answer. Below you will find the related info.

Bacnet 20180301
FW 20180822
Reply
#13
I would start from upgrading to RC3
------------------------------
Ctrl+F5
Reply
#14
(06.01.2021, 09:20)Daniel. Wrote: I would start from upgrading to RC3

Hi Daniel . 
I have just upgraded to RC3. Unfortunately same result .
Searching procedure takes place a couple of minutes but nothing happens.
Reply
#15
Run WireShark with filter set to "udp.port==0xBAC0" and check if you have any Who-Has requests.
Reply
#16
(11.01.2021, 08:52)admin Wrote: Run WireShark with filter set to "udp.port==0xBAC0" and check if you have any Who-Has requests.

You can check at the attached screenshots that 10.10.10.35 asks with a who-is message and 10.10.10.36, 37, 11,12,13,14,19 returns an I am response .
Nevertheless, at LM no device is appearing.

Attached Files Thumbnail(s)
       
Reply
#17
Try genohm-scada-bacnet instead of the BACnet client application. Remove the app then install the package from here: https://dl.openrb.com/lm-20-imx6/pkg/
Reply
#18
Hello Admin and Daniel,

Can the Bacnet client be used to read (get the bacnet IP values and translate it to knx values) and write (get the knx values and translate them to bacnet IP)?

Could I use the Bacnet Server to implement the functions above? Or there is a need of two LMs running one in client mode and one in server mode?

What I need to achieve in the end is a full bi-directional communication with a BMS server over bacnet IP. So that all statuses and feedback values can be sent to the BMS server from the KNX and also commands (binary and setpoint values) from the BMS server sent to the KNX.

Is there a limitation for the datapoints for this?


Kind regards.
Reply
#19
If your BMS server has bacnet client then just export objects and set bacnet server in LM. Communication will be both ways.
------------------------------
Ctrl+F5
Reply
#20
(22.02.2021, 12:55)Daniel. Wrote: If your BMS server has bacnet client then just export objects and set bacnet server in LM. Communication will be both ways.

Thanks for the quick reply. Is there a limit on datapoints? 

On the bacnet client side (BMS Server) is the polling necessary to recieve the feedbacks and vice-versa for the LM to get the settpoints or everything is updated on value change automatically?

Kind Regards.