17.06.2021, 12:42
I am using the PID function in FB editor but it is not calculating a value for valve opening. Anybody experienced this before?
PID in FB editor
17.06.2021, 12:42
17.06.2021, 14:06
As far I know FB PID is based on our script version. Have a read trough these threads and it should help you to debug it.
https://forum.logicmachine.net/showthrea...0#pid20270 https://forum.logicmachine.net/showthrea...1#pid20501
17.06.2021, 16:34
I get no output at all. I also removed the PID in FB editor and tried with this info https://openrb.com/example-pid-thermostat-with-lm2/
added the PID to the User Libraries Code: PID = {
-- default params
defaults = {
-- invert algorithm, used for cooling
inverted = true,
-- minimum output value
min = 0,
-- maximum output value
max = 100,
-- proportional gain
kp = 0.25,
-- integral gain
ki = 0.42,
-- derivative gain
kd = 0.1,
-- PID init, returns new PID object
function PID:init(params)
local n = setmetatable({}, { __index = PID })
local k, v
-- set user parameters
n.params = params
-- copy parameters that are set by user
for k, v in pairs(PID.defaults) do
if n.params[ k ] == nil then
n.params[ k ] = v
-- reverse gains in inverted mode
if n.params.inverted then
n.params.kp = -n.params.kp
n.params.ki = -n.params.ki
n.params.kd = -n.params.kd
return n
-- resets algorithm on init or a switch back from manual mode
function PID:reset()
-- previous value
self.previous = grp.getvalue(self.params.current)
-- reset iterm
self.iterm = 0
-- last running time
self.lasttime = os.time()
-- clamp iterm
self:clampiterm()
-- clamps iterm value
function PID:clampiterm()
self.iterm = math.max(self.iterm, self.params.min)
self.iterm = math.min(self.iterm, self.params.max)
-- clamp and set new output value
function PID:setoutput()
local t, object, value
self.output = math.max(self.output, self.params.min)
self.output = math.min(self.output, self.params.max)
value = math.floor(self.output)
local t = type(self.params.output)
-- write to output if object is set
if t == 'string' or t == 'table' then
if t == 'string' then
self.params.output = { self.params.output }
for _, output in ipairs(self.params.output) do
grp.write(output, value, dt.scale)
-- algorithm step, returns nil when disabled or no action is required, output value otherwise
function PID:run()
local result
-- get manual mode status
local manual = self.params.manual and grp.getvalue(self.params.manual) or false
-- in manual mode, do nothing
if manual then
self.running = false
-- not in manual, check if reset is required after switching on
elseif not self.running then
self:reset()
self.running = true
-- compute new value if not in manual mode
if self.running then
-- get time between previous and current call
local now = os.time()
self.deltatime = now - self.lasttime
self.lasttime = now
-- run if previous call was at least 1 second ago
if self.deltatime > 0 then
result = self:compute()
return result
-- computes new output value
function PID:compute()
local current, setpoint, deltasc, deltain, output
-- get input values
current = grp.getvalue(self.params.current)
setpoint = grp.getvalue(self.params.setpoint)
-- delta between setpoint and current
deltasc = setpoint - current
-- calculate new iterm
self.iterm = self.iterm + self.params.ki * self.deltatime * deltasc
self:clampiterm()
-- delta between current and previous value
deltain = current - self.previous
-- calculate output value
self.output = self.params.kp * deltasc + self.iterm
self.output = self.output - self.params.kd / self.deltatime * deltain
-- write to output
self:setoutput()
-- save previous value
self.previous = current
return self.output
endand added the following script to the Resident Scripts Code: -- init pid algorithm
if not p then
p = PID:init({
current = '2/2/8',
setpoint = '32/1/58',
output = '32/1/58'
-- run algorithm
p:run()But my output stays 0. I want to control a 3 way valve at the output to get a stable temperature at the valve for cooling. Current is the measured flow temperature Setpoint the requested flow temperature and Output is 0-100% (0-10V)
18.06.2021, 07:46
Your setpoint and the output is same group. For PID to work it must be live device with real feedback.
18.06.2021, 09:21
(18.06.2021, 07:46)Daniel. Wrote: Your setpoint and the output is same group. For PID to work it must be live device with real feedback. OK, that was the problem, live feedback was already there as it runs to a selector (different PID in cooling and heating) The problem is in the fact it can't be a virtual object. Still in FB editor it won't work. |