Posts: 7758
Threads: 42
Joined: Jun 2015
Reputation:
447
This can possibly happen if the device was powered off for a long time period. What are the settings for other trend logs?
Posts: 265
Threads: 37
Joined: Apr 2019
Reputation:
4
Hello, at the end of the month I will check again what total value is registered to see if the problem is solved with the new Firm.
Reviewing the daily data, for some reason a counter has sent an erroneous value and this has been recorded. Can it be removed or modified in any way?
Posts: 4643
Threads: 24
Joined: Aug 2017
Reputation:
207
You probably using trend type 'counter' and you had a drop in value which is not allowed there. Try using 'Counter with Negative delta' instead. No this cannot be modified.
------------------------------
Ctrl+F5
Posts: 265
Threads: 37
Joined: Apr 2019
Reputation:
4
Hello, I was waiting for a new month to start. With the new firm my problem is not solved. There is some error in the trend recording app, since the values in monthly view are being recorded correctly, but in annual view the value does not correspond to the monthly table. The same thing happens as the images shared above.
Any ideas so I can fix this?
Posts: 7758
Threads: 42
Joined: Jun 2015
Reputation:
447
Can you send your backup via PM?
Posts: 7758
Threads: 42
Joined: Jun 2015
Reputation:
447
Thanks for the backup. This bug will be fixed in the next release soon. I've also noticed an issue with the counter reset in your scripts. Because scheduled scripts and trends data collection run in parallel it's possible that trends get the older values and previous month value goes into the current month. You should reset the values not exactly at 0:00 but several minutes before that.
Posts: 265
Threads: 37
Joined: Apr 2019
Reputation:
4
Hello, what total MB limitation do we have in the trend register? I had read a long time ago that this space was shortened with the last firm.
I want to log 3 4byte values per counter. (Total consumption, Monthly consumption and cost). I will have around 300 meters and surely this space will not be enough for everyone. 300x72KB = 21.6MB
Being this insufficient space, would I have to add more LMs to the installation or do we have another alternative to add more space?
Thanks
Posts: 4643
Threads: 24
Joined: Aug 2017
Reputation:
207
Having 300 trends it is significant load also for CPU. You better split this.
------------------------------
Ctrl+F5
Posts: 4643
Threads: 24
Joined: Aug 2017
Reputation:
207
The limit is 20MB but this is just not to overload memory and SPI. You also have to watch other factors like CPU load and all other stuff you will put it there. How are you going to connect 300 meters? I assume it is modbus and each line has a limit of 31. OK we do not limit this in LM but this is modbus specification. The reading from so many meters will be also a slow process.
------------------------------
Ctrl+F5
Posts: 4643
Threads: 24
Joined: Aug 2017
Reputation:
207
You should be OK with 2
------------------------------
Ctrl+F5