Mqtt broker app communication with local client event based script
broker = "localhost"
port = 1883
username = "admin"
password = "password"
topic = "casambi/1/set/target_level"
value = event.getvalue()
if value == 1
  then
payload = tostring"("level":255,"duration":1,"targetid":177,"targettype":1,)"
  payload = tostring"("level":0,"duration":1,"targetid":177,"targettype":1,)"
mqtt = require("mosquitto")
client = mqtt.new()
client.ON_CONNECT = function(status, rc, msg)
  if status then
    log("mqtt connected")
    client:publish(topic, tostring(payload))
    log("mqtt connect failed " .. tostring(msg))
    client:disconnect()
client.ON_PUBLISH = function()
  client:disconnect()
client:login_set(username, password)
status, rc, msg = client:connect(broker, port)
if status then
  client:loop_forever()
  log("connect failed: " .. tostring(msg))
Error log shows:
attempt to call global 'level' (a nil value)
stack traceback:
Your tostring() call is incorrect. If this is an event script then value is true / false not 1 / 0. Are you sure about the payload format? Is it JSON?
(13.02.2023, 12:31)admin Wrote: Your tostring() call is incorrect. If this is an event script then value is true / false not 1 / 0. Are you sure about the payload format? Is it JSON?
Yes the paylod format is in JSON format
value = event.getvalue() level = value and 255 or 0 payload = require('json').encode({   level = level,   duration = 1,   targetid = 177,   targettype = 1, }) mqtt = require("mosquitto")
Thank you admin it's working. but for to get the data from mqtt server in json and load the particular data in group address on event based script.
See this example: https://forum.logicmachine.net/showthrea...6#pid10926