Convert RGBW 1byte in to DT8 object
Hello Dears,
I want to create a script that convert 4x1byte objects in to 1 DT8 object.
but how to avoid multiple write to the DALI: like if the 4 RGBW objects changed this will trigger 4 DT8 Commands to the DALI Bus!
Could you share a script considering this case.
Best Regards,
Use a single event script for all 4 objects via a common tag. Set execution mode to "Last instance only". Add a small delay before writing to the RGBW object.
thanks
could you share a starting example
also how to read the GA name from script?
Best Regards,
Adjust sleep time as needed. Higher value will prevent duplicate messages but will add a visible delay to the light changes. Separate script is needed for each R/G/B/W + RGBW objects.
Code for 6 byte DALI RGBW output object:
os.sleep(0.5) value = {   red = grp.getvalue('1/1/1') * 2.55,   green = grp.getvalue('1/1/2') * 2.55,   blue = grp.getvalue('1/1/3') * 2.55,   white = grp.getvalue('1/1/4') * 2.55, } grp.write('1/1/5', value)
Use this to find the source object name:
obj = grp.find(event.dst) log(obj.name)
Thank you admin
Very helpful
Best Regards,
Dear admin
If I want to convert from DT8 to R,G,B,W 1byte for status feedback, Should I divide by 2.55?
Best Regards,
Yes, if 1 byte objects use scale (0..100) data type.
(19.04.2023, 07:41)admin Wrote: Yes, if 1 byte objects use scale (0..100) data type.
I use 1byte unsigned integer not scale, so do I need to multiple and divide by 2.55 in both Control and status scripts?
or should I use the scale object instead?
Best Regards,
DALI RGBW data type uses 0..255 range for each channel. If you 1 byte objects use the same range then you don't have to divide or multiply.