SAKURA VRF
Hello dears,
Does any one connect to SAKURA VRF System?
is it possible to make the bit mask for the R/W holding register using profile?
.pdf   Datsheet.pdf (Size: 2.68 MB / Downloads: 3)
.xlsx   NEW MODBUS TABLE.xlsx (Size: 40.33 KB / Downloads: 4)
Best Regards,
See this: https://forum.logicmachine.net/showthrea...te_bitmask
Most likely the real address of this holding register is 0 not 40001.
Should this Work?
{       "name": "On Off",   "address": 0,   "value_custom": { "1": "Off", "2": "On" },       "bus_datatype": "uint8",       "datatype": "uint16",       "type": "register",   "value_bitmask": 0xC000,   "writable": true,       "write_bitmask": true     }
Best Regards,
First check if Read test works so you know that you talk to correct register, then make full profile and test, looks ok.