(19.09.2023, 07:37)admin Wrote: Are you using LM as a client? Is BACnet server disabled in LM? Can you discover objects using YABE?
Hi, I am using the package inside LM and not the application (Bacnet Client) from the "store". But now I am getting the objects, but when I change the values from my ventilation app(Flexit Go), the register doesn't update.
I have set 1994 to 16, but it is still 17. (Attached image)
(19.09.2023, 07:37)admin Wrote: Are you using LM as a client? Is BACnet server disabled in LM? Can you discover objects using YABE?
Hi, I am using the package inside LM and not the application (Bacnet Client) from the "store". But now I am getting the objects, but when I change the values from my ventilation app(Flexit Go), the register doesn't update.
I have set 1994 to 16, but it is still 17. (Attached image)
The value won't update automatically, you need to manually press scan. Mapping to objects has to be done via scripts. If you have several BACnet scripts running in parallel then direct connection must be used, see this post for an example: https://forum.logicmachine.net/showthread.php?tid=4530
As mentioned before if you want to use read/write in parallel then use direct connection mode. Check if there's another value on your device with a priority lower than 13. Check the result/error when writing (adjust device IP as needed):
(21.09.2023, 10:22)admin Wrote: As mentioned before if you want to use read/write in parallel then use direct connection mode. Check if there's another value on your device with a priority lower than 13. Check the result/error when writing (adjust device IP as needed):