Use this:
12345678910111213141516171819
--Best way is to tag your objects with a specific tag for each different COV value and then run this script once: covincr = 0.1 tag = 'mycovtag1' db:query('UPDATE objects SET covincr=? WHERE id IN (SELECT object FROM objecttags WHERE tag=?)', covincr, tag) covincr = 0.5 tag = 'mycovtag2' db:query('UPDATE objects SET covincr=? WHERE id IN (SELECT object FROM objecttags WHERE tag=?)', covincr, tag) os.execute('/etc/init.d/bacnet restart') script.disable(_SCRIPTNAME) --or covincr = 0.1 db:query('UPDATE objects SET covincr=? WHERE export = 1', covincr) os.execute('/etc/init.d/bacnet restart') script.disable(_SCRIPTNAME)