LM Modbus Integration with Daikin D3 Net
We are trying to connect Daikin Split AC (17 no's) to Logic machine. We have a Daiken D3 Gateway which has a Modbus port. Each AC unit has 5 no's input registers, example - 32001 (On Off Status), 32002 (Operation Mode Status) to 32005 (Room Temperature) and 3 no's holding registers, example - 42001 (On Off), 42002 (Operation Mode) to 42003 (Temperature Setpoint).
Daikin has confirmed that we should poll only 10 Modbus registers at a time (so that there is no delay).
We need a script which can read 10 registers at a time. The next 10 registers should be read with a delay of 3-4 secs.
All Daikin split ACs are wired on a two-wire bus in loop-in, loop-out manner (like a BUS & not star architecture). At the end of the BUS there is a gateway called D3 from Daikin.
.xlsx   Copy_of_Dr._Achit_Rao_kurnool.xlsx (Size: 27.84 KB / Downloads: 4)
You can add read_delay to the profile and it will wait  as much as you specify. To read 10 registers at once use block read, see this
https://forum.logicmachine.net/showthrea...9#pid30319
https://forum.logicmachine.net/showthrea...8#pid19268
Reading multiple registers can also be done via a script. Use mbproxy as suggested earlier.
-- read 10 registers starting with address 5374 res = { mb:readregisters(5374, 10) } -- read ok if res[ 1 ] then   log(res) end
There is a 404 error for the links shared.
I corrected the links but my solution will not work, forgot that read_delay max value is 1s, use script as Admin suggested