This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

dim up / down to percentage
#1
I run this script to change up/down dim to a percentage but when it runs the logic machine goes in overload (100%) Is there another/better way?

Code:
123456789101112131415161718192021222324
dimmer = grp.getvalue('1/3/10') step = bit.band(dimmer, 0x07) if step ~= 0 then   addr = '1/4/10'   up = bit.band(dimmer, 0x08) ~= 0   value = grp.getvalue(addr)   if up then     newvalue = value + 5   else     newvalue = value - 5   end   -- clamp between 0 and 100   newvalue = math.min(newvalue, 100)   newvalue = math.max(newvalue, 0)   if newvalue ~= value then     grp.write(addr, newvalue)   end end os.sleep(0.2)
Reply
#2
You probably run this as resident script at 0 sec correct?

Or do you have it as event based attached to 1/4/10?

If yes then you should change that as this way you run this script every 0.2 seconds..
Reply
#3
Yep run it as resident and as long as I touch no button it is fine. When I change something everything gets slow
Reply
#4
Use an event script with execution mode set to "Last instance only".
Code:
12345678910111213141516171819202122232425262728
out = '32/0/25' dimmer = event.getvalue() step = bit.band(dimmer, 0x07) if step == 0 then   return end up = bit.band(dimmer, 0x08) ~= 0 vstep = up and 5 or -5 value = grp.getvalue(out) while true do   nvalue = value + vstep   nvalue = math.min(nvalue, 100)   nvalue = math.max(nvalue, 0)   if nvalue ~= value then     grp.write(out, nvalue)     value = nvalue     os.sleep(0.2)   else     break   end end

What do you mean by everything gets slow? The script sends 5 telegrams per second which is not a high load. You can lower this by increasing the sleep time. You might need to adjust the step size to keep the dimming speed the same as before.
Reply
#5
Slow i mean TP Load goes to 100%
Reply
#6
Connect ETS group monitor and see what you get there. If there's another KNX/IP interface on the same TP line you might get a loop where each message is repeated several times before the hop counter becomes 0.