Trend evaluation
 I would like to automatically evaluate my trend recording. I have a consumption counter that is reset daily at 0:00. I would like to have an evaluation on which day was the highest consumption and the consumption value.
See examples here:
https://kb.logicmachine.net/libraries/trends/#examples
https://forum.logicmachine.net/showthrea...84#pid4484
Not quite what I'm looking for, I just want to get the day with the highest value.
day 1 5kw, day 2 7kw, day 3 6 Kw, day 4 10 Kw, day 5 3 kw etc., should then show me that day 4 with 10kw was the highest value
This will log the highest value and respective date for the past 7 days.
12345678910111213141516171819
daycount = 7 trendname = 'TEMP' dates = {} dates['start'] = os.date('*t') dates['start'].day = dates['start'].day - daycount dates['end'] = os.date('*t') values = require('trends').fetch(trendname, dates, 86400, true) table.sort(values, function(a, b)   return a[2] > b[2] end) max = values[ 1 ] time, value = unpack(max) date = os.date('%F', time) log(date, value)
I have now solved it like this, I get the value as a KNX object
if event.getvalue() > grp.getvalue('55/0/4') then
grp.update('55/0/4', event.getvalue())
grp.update('55/0/5', os.date(' %A %d %B %H:%M '))