troubleshooting modbus script to control fornius inverter
due to dynamic energy prices I wan't to enable / disable throttle of the inverter. This is possbile via modbus. Unfortunatelly it's not working and I have nothing in the log of LM.
require('luamodbus') mb = luamodbus.tcp() mb:open('192.168.1.111', 502) mb:connect() res, err = mb:connect() if res then     if (value <35) then     r0 = mb:writeregisters(40236, 0)         log(r0, '<')              else     r1 = mb:writeregisters(40236, 0)       r2 = mb:writeregisters(40232, 10000)       r3 = mb:writeregisters(40236, 1)        log(r1, r2, r3 '>')       mb:close()     end else   log('failed', err) end
Log if value <35
* arg: 1
  * nil
* arg: 2
  * string: <
=> This seems to work
Log if value >35
Nothing in the log and I don't know why.
Any idea what could be wrong?
You have two connect calls, remove one of them. Then log the error returned by the write call:
r0, err = mb:writeregisters(40236, 0) log(r0, err)
Same for all other registers.
Thanks, that was an error as well. If someone what's to set the softlimit from a fronius inverter depending on the enery prices, this is the clean code:
t = os.date ("*t") value = grp.getvalue('34/1/' .. t.hour) require('luamodbus') mb = luamodbus.tcp() mb:open('192.168.1.111', 502) res, err = mb:connect() mb:setslave(1) if res then     if (value <35) then         mb:writeregisters(40236, 0)         log('PV softlimit')         else     mb:writeregisters(40236, 0)       mb:writeregisters(40232, 10000)       mb:writeregisters(40236, 1)        log('PV unlimited')            end     mb:close()   else   log('failed', err) end