This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

KNX/TP: Disconnected
#1
Hi,
We've have a device that has been working fine for years, and now is getting this alerts:
   

When connecting to the bus (through LM) using ETS, and when we read device states, most responses are lost... 
Can it be a SD card issue? Or what can be happening?

Thanks.
Reply
#2
It is most likely too big bus traffic.
------------------------------
Ctrl+F5
Reply
#3
(16.10.2024, 12:48)Daniel Wrote: It is most likely too big bus traffic.

But when I connect using ETS I can't see a lot of traffic...
Reply
#4
What is the bus voltage next to LM? Check the KNX connector.
------------------------------
Ctrl+F5
Reply
#5
(16.10.2024, 15:20)Daniel Wrote: What is the bus voltage next to LM? Check the KNX connector.

30.2V
Reply
#6
Do you have another KNX psu to try?
------------------------------
Ctrl+F5
Reply
#7
(16.10.2024, 16:04)Daniel Wrote: Do you have another KNX psu to try?

Not at the moment... When I go again to the installation I'll try and let you know if it's solved or not.
Thanks.
Reply