the average value of tagged objects
#21
You need to assign a common tag to all inputs that belong to a single gate. Make sure that output object is not tagged.
(18.10.2024, 06:10)admin Wrote: You need to assign a common tag to all inputs that belong to a single gate. Make sure that output object is not tagged.
Can you send an example to me?
In object properties there's Tags field. Each OR gate group of objects must have a unique tag.
(18.10.2024, 06:19)admin Wrote: In object properties there's Tags field. Each OR gate group of objects must have a unique tag.
Maybe I´m the stupid, but I dont know how to assign group adresses ('2/2/1','2/2/3','2/2/4','2/2/5','2/2/6','2/2/7','2/2/8','2/2/9','2/2/10','2/2/11','2/2/12','2/2/13','2/2/14') to tag group
Go to Objects tab, click 2/2/1 to open Edit object form and set Tags field to group_1. Do this for all other objects from the same group.
You can use Object filter and Mass edit to assign tags to multiple objects at once.
(18.10.2024, 06:37)admin Wrote: Go to Objects tab, click 2/2/1 to open Edit object form and set Tags field to group_1. Do this for all other objects from the same group.
ok, i do this but something is wrong because error of nill compare
123456789101112131415161718192021222324252627282930313233343536373839404142434445464748495051525354555657585960616263646566676869707172737475767778798081828384858687888990919293949596979899100101102103104105106107108109110111112113114115116117118119120121122123124125126127128129130131132133134135136137138139140141142143144145146147148149150151152153154155156157158159160161162163164165166167168169170171172173174175176177178179180181182183184185186187188189190191192193194195196197198199200201202203204205206207208209210211212213214215
if not client then   -- each group has 3 fields:   -- tag - status object tag   -- output - status output object   -- mode - calculate mode (and/or/avg)   groups = {     { tag = 'vnt251', output = '6/2/51', mode = 'or' },     { tag = 'vnt252', output = '6/2/52', mode = 'or' },     { tag = 'vnt254', output = '6/2/54', mode = 'or' },     { tag = 'vnt150', output = '6/1/50', mode = 'or' },     { tag = 'vnt152', output = '6/1/52', mode = 'or' },     { tag = 'vnt153', output = '6/1/53', mode = 'or' },   }       -- time to wait between last telegram from any status in group and update   updatedelay = 0.5   timeout = updatedelay / 2   -- object value cache   values = {}   -- object datatype cache   datatypes = {}   -- send update only when value changes   grp.checkupdate = function(alias, value)     if values[ alias ] ~= value then       grp.update(alias, value)     end   end   calc = {}   -- AVERAGE value   calc['avg'] = function(group)     local result, count, value = 0, 0     for _, address in ipairs(group.objects) do       value = values[ address ]       -- number must be in [0..100] range       if type(value) == 'number' then         result = result + value         count = count + 1       -- boolean true is 100%, false is 0%       elseif type(value) == 'boolean' then         if toboolean(value) then           result = result + 100         end         count = count + 1       end     end     if count > 0 then       result = math.floor(result / count + 0.5)       grp.checkupdate(group.output, result)     end   end   -- AND gate   calc['and'] = function(group)     local result = true     for _, address in ipairs(group.objects) do       result = result and toboolean(values[ address ])     end     grp.checkupdate(group.output, result)   end   -- OR gate   calc['or'] = function(group)     local result = false     for _, address in ipairs(group.objects) do       result = result or toboolean(values[ address ])     end     grp.checkupdate(group.output, result)   end   -- MAX value   calc['max'] = function(group)     local result = -math.huge     for _, address in ipairs(group.objects) do       local value = values[ address ]       if type(value) == 'number' then         result = math.max(result, value)       end     end     grp.checkupdate(group.output, result)   end   -- MIN value   calc['min'] = function(group)     local result = math.huge     for _, address in ipairs(group.objects) do       local value = values[ address ]       if type(value) == 'number' then         result = math.min(result, value)       end     end     grp.checkupdate(group.output, result)   end   -- SUM value   calc['sum'] = function(group)     local result = 0     for _, address in ipairs(group.objects) do       local value = values[ address ]       if type(value) == 'number' then         result = result + value       end     end     grp.checkupdate(group.output, result)   end   -- prepare each group   for _, group in ipairs(groups) do     object = grp.find(group.output)     -- cache output status object value and datatype     values[ object.address ] = object.data     datatypes[ object.address ] = object.datatype     group.output = object.address     -- group input status object list     group.objects = {}     -- find all status objects and cache values and datatypes     objects = grp.tag(group.tag)     for _, object in ipairs(objects) do       values[ object.address ] = object.data       datatypes[ object.address ] = object.datatype       table.insert(group.objects, object.address)     end     -- force update on first run     group.timer = 0     -- calc function reference     group.fn = calc[ group.mode ]   end   -- handle group writes   function eventhandler(event)     local dst, datatype     dst = event.dst     datatype = datatypes[ event.dst ]     -- unknown object, stop     if not datatype then       return     end     values[ dst ] = dpt.decode(event.datahex, datatype)     -- check if any group needs to be updated     for _, group in ipairs(groups) do       for _, address in ipairs(group.objects) do         if address == dst then           group.timer = updatedelay         end       end     end   end   require('genohm-scada.eibdgm')   client = eibdgm:new({ timeout = 0.1 })   client:sethandler('groupwrite', eventhandler) end delta = 0 repeat   tsec, tusec = os.microtime()   client:step()   tdelta = os.udifftime(tsec, tusec)   -- clock jump   if tdelta < 0 then     delta = timeout   else     delta = delta + tdelta   end until delta >= timeout -- check if any group has an active timer for _, group in ipairs(groups) do   timer = group.timer   if timer then     timer = timer - delta     -- timer expired, run calc function     if timer <= 0 then       group.fn(group)       timer = nil     end     group.timer = timer   end end
most likely a tag is assigned to wrong object
(18.10.2024, 08:47)Daniel Wrote: most likely a tag is assigned to wrong object
All off objects are 1.bit switch and output too
send me your backup to PM
Disable Autoload for this user library Dobeh_ventilatoru
add require('user.Dobeh_ventilatoru') in every script you want this to run
(18.10.2024, 11:00)Daniel Wrote: Disable Autoload for this user library Dobeh_ventilatoru
Ok, but error message from script "Svetla pro ventilátory" is still there.
Disable and enable this script to restart it.
(21.10.2024, 07:49)Daniel Wrote: Disable and enable this script to restart it.
Restart of script doesnt work, after restart LM, it works fine. Thank for Your help.
