the average value of tagged objects
#21
You need to assign a common tag to all inputs that belong to a single gate. Make sure that output object is not tagged.
(18.10.2024, 06:10)admin Wrote: You need to assign a common tag to all inputs that belong to a single gate. Make sure that output object is not tagged.
Can you send an example to me?
In object properties there's Tags field. Each OR gate group of objects must have a unique tag.
(18.10.2024, 06:19)admin Wrote: In object properties there's Tags field. Each OR gate group of objects must have a unique tag.
Maybe I´m the stupid, but I dont know how to assign group adresses ('2/2/1','2/2/3','2/2/4','2/2/5','2/2/6','2/2/7','2/2/8','2/2/9','2/2/10','2/2/11','2/2/12','2/2/13','2/2/14') to tag group
Go to Objects tab, click 2/2/1 to open Edit object form and set Tags field to group_1. Do this for all other objects from the same group.
You can use Object filter and Mass edit to assign tags to multiple objects at once.
(18.10.2024, 06:37)admin Wrote: Go to Objects tab, click 2/2/1 to open Edit object form and set Tags field to group_1. Do this for all other objects from the same group.
ok, i do this but something is wrong because error of nill compare
if not client then
  -- each group has 3 fields:
  -- tag - status object tag
  -- output - status output object
  -- mode - calculate mode (and/or/avg)
  groups = {
    { tag = 'vnt251', output = '6/2/51', mode = 'or' },
    { tag = 'vnt252', output = '6/2/52', mode = 'or' },
    { tag = 'vnt254', output = '6/2/54', mode = 'or' },
    { tag = 'vnt150', output = '6/1/50', mode = 'or' },
    { tag = 'vnt152', output = '6/1/52', mode = 'or' },
    { tag = 'vnt153', output = '6/1/53', mode = 'or' },
  -- time to wait between last telegram from any status in group and update
  updatedelay = 0.5
  timeout = updatedelay / 2
  -- object value cache
  values = {}
  -- object datatype cache
  datatypes = {}
  -- send update only when value changes
  grp.checkupdate = function(alias, value)
    if values[ alias ] ~= value then
      grp.update(alias, value)
  calc = {}
  -- AVERAGE value
  calc['avg'] = function(group)
    local result, count, value = 0, 0
    for _, address in ipairs(group.objects) do
      value = values[ address ]
      -- number must be in [0..100] range
      if type(value) == 'number' then
        result = result + value
        count = count + 1
      -- boolean true is 100%, false is 0%
      elseif type(value) == 'boolean' then
        if toboolean(value) then
          result = result + 100
        count = count + 1
    if count > 0 then
      result = math.floor(result / count + 0.5)
      grp.checkupdate(group.output, result)
  -- AND gate
  calc['and'] = function(group)
    local result = true
      result = result and toboolean(values[ address ])
  -- OR gate
  calc['or'] = function(group)
    local result = false
      result = result or toboolean(values[ address ])
  -- MAX value
  calc['max'] = function(group)
    local result = -math.huge
      local value = values[ address ]
        result = math.max(result, value)
  -- MIN value
  calc['min'] = function(group)
    local result = math.huge
        result = math.min(result, value)
  -- SUM value
  calc['sum'] = function(group)
    local result = 0
  -- prepare each group
  for _, group in ipairs(groups) do
    object = grp.find(group.output)
    -- cache output status object value and datatype
    values[ object.address ] = object.data
    datatypes[ object.address ] = object.datatype
    group.output = object.address
    -- group input status object list
    group.objects = {}
    -- find all status objects and cache values and datatypes
    objects = grp.tag(group.tag)
      table.insert(group.objects, object.address)
    -- force update on first run
    group.timer = 0
    -- calc function reference
    group.fn = calc[ group.mode ]
  -- handle group writes
  function eventhandler(event)
    local dst, datatype
    dst = event.dst
    datatype = datatypes[ event.dst ]
    -- unknown object, stop
    if not datatype then
      return
    values[ dst ] = dpt.decode(event.datahex, datatype)
    -- check if any group needs to be updated
        if address == dst then
          group.timer = updatedelay
  client = eibdgm:new({ timeout = 0.1 })
  client:sethandler('groupwrite', eventhandler)
delta = 0
repeat
  tsec, tusec = os.microtime()
  client:step()
  tdelta = os.udifftime(tsec, tusec)
  -- clock jump
  if tdelta < 0 then
    delta = timeout
    delta = delta + tdelta
until delta >= timeout
-- check if any group has an active timer
  timer = group.timer
  if timer then
    timer = timer - delta
    -- timer expired, run calc function
    if timer <= 0 then
      group.fn(group)
      timer = nil
    group.timer = timer
most likely a tag is assigned to wrong object
(18.10.2024, 08:47)Daniel Wrote: most likely a tag is assigned to wrong object
All off objects are 1.bit switch and output too
send me your backup to PM
Disable Autoload for this user library Dobeh_ventilatoru
add require('user.Dobeh_ventilatoru') in every script you want this to run
(18.10.2024, 11:00)Daniel Wrote: Disable Autoload for this user library Dobeh_ventilatoru
Ok, but error message from script "Svetla pro ventilátory" is still there.
Disable and enable this script to restart it.
(21.10.2024, 07:49)Daniel Wrote: Disable and enable this script to restart it.
Restart of script doesnt work, after restart LM, it works fine. Thank for Your help.