snmpv3 authPriv issue
Hello to all,
I have been working in the last period to integrate a series of UPS of APC using the snmp protocol.
The version required is v3.
I have used this site: http://luasnmp.luaforge.net/objects.html to get information for the parameters of snmp.
ups1, err = snmp.open{
    version = snmp.SNMPv3,
  community = "public",
  port = 161,
  peer = "IP address",
  user = "Sotirios",
  authPassphrase = "Papantoniou1",
  privPassphrase  = "Papantoniou2",
  authType = "MD5",
  privType = "AES",
  timeout = 2,
  securityLevel = "authNoPriv",--"noAuthNoPriv",
assert(ups1, err)
log(ups1)
log(err)
local OID_NAS3 = {
    {'Varname',"1.3.6.1.4.1.935.1.1.1.1.1.1.0"},--NEW
  for _, item in ipairs(OID_NAS3) do
    vbind, err = ups1:get(item[2])
    if vbind then
    log(vbind.value)
      log('error reading from snmp: ' .. tostring(err))
      --grp.checkwrite('EL_UPS_communication_KO',true)
On security level when I am using noAuthNoPriv or authNoPriv everything is working correctly. When I use authPriv adding all the parameters correctly (cross-checked with other 3rd party software) I have problem with the communication.
The log message I got was:
error reading from snmp: snmp: internal error - synch request id is 0
This error arrives even when the parameters I have inserted are wrong. Google searching:"synch request id is 0"  I have found the error on the source code but no explanation why this is happening.https://github.com/hleuwer/luasnmp/blob/.../nm_snmp.c
Has anybody else found a similar problem? How can I solve this issue?
Thank you
Sotiris
Current version of SNMP library does not have encryption support. We'll try to update it for the next FW release.
(07.05.2020, 07:46)admin Wrote: Current version of SNMP library does not have encryption support. We'll try to update it for the next FW release.
Hello admin,
thank you for the answer. Do you have an estimation on when the next FW release will be?
Thank you
Sotiris
Hi, i'm testing 2 identical UPS like the post above ( one with a new network card and one with old model )
After get function with old network card everything is working and the log of the variable vbind is:
* table:
["oid"]
  * string: 1.3.6.1.4.1.935.1.1.1.8.6.1.0
["type"]
  * number: 3
["value"]
  * number: 16
with the new network card and new oid the log is:
* table:
["oid"]
  * string: 1.3.6.1.4.1.318.1.1.1.9.2.2.1.4
["type"]
  * number: 129
i don't have the row value... any idea?
From PC and MibBrowser everithing is ok, the only thing is when i load the MIB file of the UPS the software ask me to load also SNMP-FRAMEWORK-MIB.mib
Are you sure that OID is correct? 129 is No such instance exception.
Now i try another OID, this is the result:
table:
["oid"]
  * string: 1.3.6.1.4.1.318.1.1.1.1.2.9
["type"]
  * number: 129
attached the same OID from MibBrowser
i'm working with SL 2.8.0 + libnetsnmp_5.4.4-1_imx6.ipk + luasnmp_1.0.6-2-4_imx6.ipk
Try running walk on higher OID levels like "1.3.6.1.4.1.318.1.1.1.1": https://forum.logicmachine.net/showthrea...k#pid15779
(31.10.2024, 10:53)admin Wrote: Try running walk on higher OID levels like "1.3.6.1.4.1.318.1.1.1.1": https://forum.logicmachine.net/showthrea...k#pid15779
ok i will try in the afternoom, it works also with SNMPv3 ?
ok, from oid '1.3.6.1.4.1.318.1.1.1.1' i'm reading something:
* table:
["1.3.6.1.4.1.318.1.1.1.1.2.3.0"]
* string: 9E2234T15816
["1.3.6.1.4.1.318.1.1.1.1.2.9.0"]
* string: 10000
["1.3.6.1.4.1.318.1.1.1.1.2.1.0"]
* string: V55.006.044/V55.006.040
["1.3.6.1.4.1.318.1.1.1.1.2.5.0"]
* string: 10KH
["1.3.6.1.4.1.318.1.1.1.1.1.1.0"]
* string: Easy UPS 3S 10K
This means that instead of 1.3.6.1.4.1.318.1.1.1.1.2.9 you should use 1.3.6.1.4.1.318.1.1.1.1.2.9.0 (.0 added at the end)