communication between wiser for knx, smartmeter 85A and actuator interra 8Ch
Morning everybody
I'm a beginner on wiser for knx. I want to read data sent from smartmeter 85A and then send instructions to an actuator interra 8CH depending on what i received from smartmeter 85A
If both values are already mapped to group addresses then you need an event script attached to the meter data output group address.
This example will send true (ON) to 1/1/2 when the input value is larger than 100, false (OFF) otherwise.
value = event.getvalue() if value > 100 then   output = true else   output = false end grp.write('1/1/2', output)
(13.02.2025, 11:32)admin Wrote: If both values are already mapped to group addresses then you need an event script attached to the meter data output group address.
thanks for the reply
now, i just have programs in ETS application for smartmeter 85A (he give active power measured) and actuator. How to link all of them, so that they can send data each other ?
You must import ETS project to LM and then create event based script on your active power object, paste this script and change 1/1/2 to the actuator group
Also use grp.checkwrite() instead of grp.write() to avoid sending true or false to the bus over and over again when within range..
(13.02.2025, 11:44)Daniel Wrote: You must import ETS project to LM and then create event based script on your active power object, paste this script and change 1/1/2 to the actuator group
if the group adress linked with smartmeter is '0/0/1', can i change the line "value = event.getvalue()" by "value = grp.getvalue('0/0/1')" ?
if the event script is created on group 0/0/1 then both commands are equal.
here is the place to import ETS project ?
(13.02.2025, 13:34)Daniel Wrote: if the event script is created on group 0/0/1 then both commands are equal.
please, what is the next step to run the script ? how can i ensure "Active_power = event.getvalue()" will always read data from smartmeter ?
yes, each time your meter will send new value then the script will run. You can test it by selecting run script button.
Now i run script with infinite loop and i don't know how to stop it
Disable script and reboot lm. Do not write to the same group which is triggering the script
Hello everybody
Is this possible to make one script based event and one another resident, and share one variable in the both ?
I meant, share the same variable in the both ?
Use storage or virtual group.
Please, can you be more explicit ?
Click on Storage in script helpers.
how to proceed if i want to talk with an solar inventer ?
I mean, i want to send and receive data packet with a solar energy system using modbus
Morning everyone